< 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly">根据以上电流量查表可知,选用<FONT face="Times New Roman">BLV</FONT>导线,截面为<FONT face="Times New Roman">4×180mm<SUP>2</SUP></FONT>,其允许电流为<FONT face="Times New Roman">465A</FONT>><FONT face="Times New Roman">454.6A</FONT>,可以满足要求。<o:p></o:p></P>
<P 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly">中性线选择小<FONT face="Times New Roman">1</FONT>号<FONT face="Times New Roman">90mm<SUP>2</SUP></FONT>,接地线选用<FONT face="Times New Roman">50mm<SUP>2</SUP></FONT>。</P>
<P 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly"> </P>
<P 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly">根据以上电流量查表可知,选用<FONT face="Times New Roman">BLV</FONT>导线,截面为<FONT face="Times New Roman">4×180mm<SUP>2</SUP></FONT>,其允许电流为<FONT face="Times New Roman">370A</FONT>><FONT face="Times New Roman">363A</FONT>,可以满足要求。<o:p></o:p></P>
<P 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly">中性线选择小<FONT face="Times New Roman">1</FONT>号<FONT face="Times New Roman">90mm<SUP>2</SUP></FONT>,接地线选用<FONT face="Times New Roman">75mm<SUP>2</SUP></FONT>。<o:p></o:p></P>
<P 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 22pt; mso-line-height-rule: exactly">以上摘自楼主的大作,在下不明白:同是4×180的导线,为何允许电流不同?如果我没算错,相线、中性线、接地线共6条,如何架设?另,好像没有180平方毫米规格的导线喔!希望得到楼主的指教,谢谢!</P> |
|